OID: leading . or not? #1562
LFrank2021
started this conversation in
General
Replies: 1 comment 3 replies
-
That's just the snmp response. we have no control over it, and we aren't really using MIBs for the translation. |
Beta Was this translation helpful? Give feedback.
3 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
Sorry, I have another question.
As of today I use SNMP for CDU and Sensor data.
I noticed that my newest sensor (Temp/Humidity) did not report data and the solution was to insert a leading '.' on the MIBs.
For the discovery of my CDUs I do not have the leading dot and it still works.
What is the intended way (for openDCIM)?
What is the difference (if there is one)?
Should all MIBs be entered/work the same way?
Kind regards
Frank